What type of cable(power limited or non-power limited are used for the following ckts. I know you can use thhn in some instances but disregarding that for now.
IDC/SLC ckts.
NAC ckts
24v power for fire alarm.
thanks
FPLR or FPLP (riser or plenum) are very common for fire alarm systems.
16 or 18-2 non-shielded for SLC/IDC
14-2 non-shielded for horn and strobe NACs and 24V.
16-2 Shielded for voice or audio speaker appliance
Those are typical. Voltage drop should be considered when sizing. Follow manufacturer instructions. Some SLC/IDC are shielded.
Other factors that should be considered:
?pipe or free air
?Length
?Classification of space
?Sharing an enclosure with 120V power
?Temperature and environmental conditions
?survivability requirements or project