D Dale001289 Senior Member Location Georgia Today at 10:44 AM #1 Per 2017 NEC 760; are there any circumstances where fire alarm circuits can be combined with other wiring systems?
Per 2017 NEC 760; are there any circumstances where fire alarm circuits can be combined with other wiring systems?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Today at 12:01 PM #2 Dale001289 said: Per 2017 NEC 760; are there any circumstances where fire alarm circuits can be combined with other wiring systems? Click to expand... See 760.139 for power limited fire alarm systems. In the slight chance you have a non-power limited fire alarm system see 760.48,
Dale001289 said: Per 2017 NEC 760; are there any circumstances where fire alarm circuits can be combined with other wiring systems? Click to expand... See 760.139 for power limited fire alarm systems. In the slight chance you have a non-power limited fire alarm system see 760.48,