A single break in class A fire alarm wiring knocks out the supervisory signal and sends the system into a trouble alert, but all the components continue to work because of the double feed. . But if you also get a break in either of the "backfeed" wires, you get a trouble alert and possible loss of component function. . So it would help if the 2 primary wires are separated from the 2 "backfeed" wires. . Then the possibility of simultaneous damage to both pairs is lessened.
Now I know that the backup or backfeed isn't required because it doesn't exist on a class B system. . But with class A, many people might assume they still have full component function and procrastinate repairs which might make a multiple break in a class A more serious than a break in a class B.
Is there a requirement in either NFPA70 or 72 that states that all 4 wires of a class A system can't be contained in the same raceway ?
David