T treg New member Location Los Angeles, California Aug 13, 2014 #1 Is there a reference in the NEC or NFPA to the use of 3/4" conduit for fire alarm runs?
roger Moderator Staff member Location Fl Occupation Retired Electrician Aug 13, 2014 #2 treg said: Is there a reference in the NEC or NFPA to the use of 3/4" conduit for fire alarm runs? Click to expand... No but it is a common engineering spec. Roger
treg said: Is there a reference in the NEC or NFPA to the use of 3/4" conduit for fire alarm runs? Click to expand... No but it is a common engineering spec. Roger
m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Aug 14, 2014 #3 So that means fire alarm subject to table 9?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 14, 2014 #4 m sleem said: So that means fire alarm subject to table 9? Click to expand... Yes, per the rule in 760.3(J).