Fire alarm device labeling

GrayHair

Senior Member
Location
Nashville, TN
I've been retired for several years and no longer keep up with NFPA 72, that said, I know of no such requirement. I visibly labeled all devices with Panel/Sub-panel, Loop/Zone and Device. Addressable panels usually include the device address as part of alarm/trouble history and visibly labeled devices will speed troubleshooting. Also nice for testing. :)

This was a carry-over from conventional systems where knowing the wiring sequence would allow you to locate a single fault never having to check more than 50% +1 devices.
 

iwire

Moderator
Staff member
Location
Massachusetts
Can someone tell me if there is a code requiring
installing address labels on addressable fire alarm devices? I thought I saw
this once but am having trouble locating it again
I do not believe there is such a code requirement.


But we do it because the fire department asks for it.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I do not believe there is such a code requirement.


But we do it because the fire department asks for it.
Yeah, same here. I just hate getting the "stink eye" from the AHJ, then he really starts checking things out.
 