Is there a new code that requires a disconnect next to a FA NAC Panel? The job I'm on they used a single pole switch next to the NAC panel to disconnect the 120v feed to that panel, have never seen/done that before.
Not code and likely a violation without a lock on device.
I often will install a switch by the panel(s) during installation but remove it before final inspection.
No 'lock on' device, they used a raised cover on a 4 sq box.
760.41 NPLFA Circuit Power Source Requirements.
(A) Power Source. The power source of non?power-limited
fire alarm circuits shall comply with Chapters 1 through 4, and
the output voltage shall be not more than 600 volts, nominal.
The fire alarm circuit disconnect shall be permitted to be secured
in the ?on? position. [new for 2011]