Fire Alarm Horn Strobes

Status
Not open for further replies.

CRS

Member
Location
New Milford, CT
Hello there,
Can anyone tell me if I can mount my horn strobes directly to the wall without a box. Being low voltage, am I able to bring my fire alarm cable directly to the horn strobe? Where can I find this in the code?
Thanks
 
I didn't have my book with me but...I'd set a box for (a) mounting purposes and (b) power supervision circuits or EOL circuits requiring resistors (c) future changes (d) just a good idea.:grin:
 
Some commentary from 760.52 A

Section 760.52(A) requires power-limited fire alarm circuits using non–power-limited fire alarm wiring methods and materials to be installed in accordance with 760.25. Section 760.25 requires that non–power-limited devices be mounted in accordance with Chapter 3. Section 300.11(A) requires these devices and equipment to be securely mounted. Section 300.15(B) is also referenced to require non–power-limited circuit terminations to be made in a box or conduit body. However, 300.15(E) permits devices with integral terminal enclosures and mounting brackets to be used without a box. Devices are required to be mounted on a box or conduit body where the instructions or listing indicate the use of a box. Fire alarm system components such as manual fire alarm boxes are frequently tested. Secure mounting is necessary to ensure that they will remain in place.
italics and underline mine...

Simular wording is also used in the commentary of B
Section 760.52(B) requires mechanical protection at splices and termination points. Since failure of a circuit often occurs at splices or termination points, this requirement offers more protection and strain relief for these cable connections.

Locally I am required to pipe and box everything....
 