Re: Fire Alarm Installations
Originally posted by dragonfly54:
In the nec Article 760 talks about the conductors used in fire alarm installations, but I have run into some question about the proper size allowed. My question is what is the smallest conductor that can be used and does it matter whether it's residential or commercial.
Originally posted by dragonfly54:
Thank you all for your replies, However I still don't know what to tell these person about the wiring requirements. He has been using 22/4 solid fire wire for residential installs the way I understand the code you can't use anything smaller than 18 solid. I'm I correct?
I just happened to have a copy of the NJATC's Fire Alarm Systems book lying on my desk...in it, it is noted that:
The NEC is not a design manual. In fact, the NEC will allow wiring that may not permit the fire alarm system to properly operate. An example is the use of power wiring (e.g., THHN)where the manufacturer requires twisted, sheilded pairs
If anyone has this book, check pg. 71.
What this notation is telling ME, is that you MUST consult the manufacturers instructions for the install as the NEC is not a design guide.
Probably not the answer you want to hear...but points in the right direction...you will need to calculate the voltage drop/total resistance/current etc.
Whether the install is commercial or residential *probably* doesn't make all that much of a difference - as long as the proper wiring methods are used. This is again answered by the manufacturers specifications and job specs(THHN, twisted pairs, etc; number of devices, length of run, etc).
Where/how are you arriving at your limitation of #18?(760.27(A)/T402.5)