Fire Alarm - lighting in a large conference room

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
In a large conference room with emergency lighting programmed to by pass dimmer control in the event of a power outage, does one also have a fire alarm interphase with the lighting control system such that all the lights in that room go to full brightness in the event of a fire alarm. If so, where is this defined? Is it a function of the number of people the room is designed for?
 

dkidd

Senior Member
Location
here
Occupation
PE
IBC Section 1008.2.1... For auditoriums, theaters, concert or opera halls and similar assembly occupancies,
the illumination at the walking surface is permitted to be reduced during performances by one of the following
methods provided that the required illumination is automatically restored upon activation of a premises’ fire
alarm system.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
IBC Section 1008.2.1... For auditoriums, theaters, concert or opera halls and similar assembly occupancies,
the illumination at the walking surface is permitted to be reduced during performances by one of the following
methods provided that the required illumination is automatically restored upon activation of a premises’ fire
alarm system.
It would probably be the AHJ's call as to whether a "large conference room" meets the (unspecified) requirements for "similar assembly occupancy". They should put a number on the room occupancy. If you can't measure it, you can't control it.
 