W Wiredtight Member Location Dale City Oct 25, 2010 #1 Is it required for the generator, serving light loads, to be monitored by the Fire alarm system? If so, what article?
Is it required for the generator, serving light loads, to be monitored by the Fire alarm system? If so, what article?
steve66 Senior Member Location Illinois Occupation Engineer Oct 25, 2010 #2 No, but there is a requirement for an alarm annunciator panel. NFPA 110.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Oct 25, 2010 #3 And what type of generator.... Emergency Art 700 Legally required standby Art 701 Optionally required standby Art 702 But there is no code requirement, as mentioned NFPA 110 is the standard. NEC only covers the wiring.
And what type of generator.... Emergency Art 700 Legally required standby Art 701 Optionally required standby Art 702 But there is no code requirement, as mentioned NFPA 110 is the standard. NEC only covers the wiring.