In reviewing shop drawings from a contractor it was not apparent if the submitted low voltage cabling was NPLFA or PLFA. When I go to section IV of Article 760 three different conductor/cable voltage rating are thrown around: namely 600V for NPLFA Insulated Conductors, 150V for NPLFA cables and 300V for PLFA cables.
The question is: should we ask the contractor to specifically supply fire alarm cable in lieu of simply a low voltage cable?
The question is: should we ask the contractor to specifically supply fire alarm cable in lieu of simply a low voltage cable?