The adopted building code for that jurisdiction will likely use NFPA 72 as a reference standard for this issue.
NFPA 72 Section 10.6.7.2.1 covers the capacity of the secondary power supply.
Typically not connected to a UPS in addition to the UL listed FACP power supply with batteries. The UPS is not listed for life safety type stuff.