rkeough
New member
- Location
- Macau SAR, China
Some background is necessary. The fire alarm installation in question is located overseas. Local power is 220VAC/60Hz. Contractor installed a panel that is listed for 120VAC/60 Hz - 240VAC/50Hz. Contractor decided that the best way to provide stable primary power that was to install a voltage regulator between the primary power disconnect and fire alarm panel. Problem is the voltage regulator has a receptacle outlet, and was not made to for a direct, hardwire connection. The contractor wants to connect the fire alarm panel to the voltage regulator with a Type "SO" cord with 120V, 20A male plug. Basically, he is plugging the fire alarm panel into the voltage regulator. Everything is in conduit and the voltage regulator is installed within a vented enclosure to guard against accidental disconnects and unauthorized use of the regulator for other purposes. Everything else appears code compliant; dedicated branch circuit, listed breaker locking device, everything in conduit, etc. But, this plug thing does not pass my smell test. Is this compliant? I cannot find anything that says this "plug in" approach is not NEC 70 or NFPA 72 compliant under recent editions, but then again my core competency is not the electrical code. Am I missing something? Or is this OK, just weird.