Hello.
I understand that a Class A loop is a ring. I am unsure on a few things.
Can the outgoing and return wires reside in the same conduit coming from the panel? If so then how does it get wired. Lets assume I have a 4 wire cable. Red, Black, Blue, Green wires in it.
Lets also assume I have 2 smoke detectors in this addressable system. Can someone explain or draw the wiring through the devices and conduit?
Thanks
The out and return wires can reside in the same conduit for 10 feet where they come to the FACP. After that, they need to be separated by 1 foot for vertical runs and by 4 feet for horizontal runs. There is some additional leeway:
12.3.7* Class A and Class X circuits using physical conductors
(e.g., metallic, optical fiber) shall be installed such that the out-
going and return conductors, exiting from and returning to the
control unit, respectively, are routed separately. The outgoing
and return (redundant) circuit conductors shall be permitted in
the same cable assembly (i.e., multi-conductor cable), enclosure,
or raceway only under the following conditions:
(1) For a distance not to exceed 10 ft (3.0 m) where the out-
going and return conductors enter or exit the initiating
device, notification appliance, or control unit enclosures
(2) For single raceway drops to individual devices or appliances
(3) For single raceway drops to multiple devices or appliances installed within a single room not
exceeding 1000 ft
2 (93 m
2) in area
A.12.3.7 A goal of 12.3.7 is to provide adequate separation
between the outgoing and return cables. This separation is
required to help ensure protection of the cables from physical
damage. The recommended minimum separation to prevent
physical damage is 12 in. (300 mm) where the cable is installed
vertically and 48 in. (1.22 m) where the cable is installed hori-
zontally.