Fire alarm power circuit.

Status
Not open for further replies.

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Anyone know for sure what NFPA 72 Says about power routing to FACP? Dedicated circuit, does not equal designated conduit run, or does it? Clarification would be great.
 

nhfire77

Senior Member
Location
NH
Nope , just the circuit has to be dedicated.

See(2007) 72.4.4.1.3 and 72.4.4.1.4 Specifically 72.4.4.1.4.1 and 72.4.4.1.4.2

Also review Non-power limited fire alarm circuits in article 760.
 
Last edited:

jumper

Senior Member
Anyone know for sure what NFPA 72 Says about power routing to FACP? Dedicated circuit, does not equal designated conduit run, or does it? Clarification would be great.

Do not know about 72, but NEC 2008

760.41 NPLFA Circuit Power Source Requirements.

(B) Branch Circuit. An individual branch circuit shall be
required for the supply of the power source. This branch
circuit shall not be supplied through ground-fault circuit
interrupters or arc-fault circuit interrupters.

760.121 Power Sources for PLFA Circuits.(B) Branch Circuit. An individual branch circuit shall be required for the supply of the power source. This branch
circuit shall not be supplied through ground-fault circuit
interrupters or arc-fault circuit interrupters.
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Thanks, will have to see if scope call out expands beyond 72. On a military facility, and want to be 100% sure. Hard to pull a bullet back after you squeeze the trigger...
 