Hello!
2- Questions.
1- Currently have a Fire Alarm Design which has the Pull Station is approximately 7-10 feet away from the exit door. I understand the NFPA 72 states Pull Stations should be 5 feet away from exit door. However, I believe there is an exception within NFPA 72 that states Pull Station could be relocated more than 5 feet away during a retrofit or if construction will cost high in value. I just don't remember where in the code it states that. Please advise.
2- Is it appropriate to have a splice within a Fire Alarm System. I understand the NFPA 72 is okay with it. However, would like to see if any of you more experienced folks would be fine with it.
In my opinion, I prefer not to be with it because a short would most likely be caused within the Spliced Location and afraid if the appliance would not be functional during an emergency event.
Your guys assistant is much appreciated.
2- Questions.
1- Currently have a Fire Alarm Design which has the Pull Station is approximately 7-10 feet away from the exit door. I understand the NFPA 72 states Pull Stations should be 5 feet away from exit door. However, I believe there is an exception within NFPA 72 that states Pull Station could be relocated more than 5 feet away during a retrofit or if construction will cost high in value. I just don't remember where in the code it states that. Please advise.
2- Is it appropriate to have a splice within a Fire Alarm System. I understand the NFPA 72 is okay with it. However, would like to see if any of you more experienced folks would be fine with it.
In my opinion, I prefer not to be with it because a short would most likely be caused within the Spliced Location and afraid if the appliance would not be functional during an emergency event.
Your guys assistant is much appreciated.