cce-eng
New User
- Location
- Birmingham, Alabama
- Occupation
- Engineering
Per IBC 907.2.7 a manual fire alarm system is not required for group M occupancies if less than 500 occupants and/or less than 100 occupants above or below the lowest level of exit discharge. Therefore, no fire alarm notification appliances.
If the occupant load is less than the threshold for requiring a "manual" fire alarm system, but a fire protection (sprinkler) system is installed, does the fire sprinkler system force you to provide fire alarm notification appliances throughout the facility as would be required with a fire alarm system?
I understand the fire sprinkler system has to be monitored and emergency outcall provided to a certified monitoring agency.
If the occupant load is less than the threshold for requiring a "manual" fire alarm system, but a fire protection (sprinkler) system is installed, does the fire sprinkler system force you to provide fire alarm notification appliances throughout the facility as would be required with a fire alarm system?
I understand the fire sprinkler system has to be monitored and emergency outcall provided to a certified monitoring agency.