Where in NFPA 72 or NFPA 101 is listed the requirement of fire alarm system in different bu8lding occupancy

There is nothing in NFPA 72 regarding required fire alarm systems in particular occupancies.

In NFPA 101 you will have to look under each occupancy to see what the fire alarm requirements are.
 