L LUIS FERNANDEZ Member Mar 21, 2017 #1 Where in NFPA 72 or NFPA 101 is listed the requirement of fire alarm system in different bu8lding occupancy
Where in NFPA 72 or NFPA 101 is listed the requirement of fire alarm system in different bu8lding occupancy
dkidd Senior Member Location here Occupation PE Mar 21, 2017 #2 LUIS FERNANDEZ said: Where in NFPA 72 or NFPA 101 is listed the requirement of fire alarm system in different bu8lding occupancy Click to expand... Not NFPA 72. Look in the International Building Codes. NFPA 101 does not apply too often.
LUIS FERNANDEZ said: Where in NFPA 72 or NFPA 101 is listed the requirement of fire alarm system in different bu8lding occupancy Click to expand... Not NFPA 72. Look in the International Building Codes. NFPA 101 does not apply too often.
L lowvoltageeng Member Location Arizona, United States May 31, 2017 #3 Yes, like he said. You won't find that in the 72. IBC and 101.
gadfly56 Senior Member Location New Jersey Occupation Professional Engineer, Fire & Life Safety May 31, 2017 #4 LUIS FERNANDEZ said: Where in NFPA 72 or NFPA 101 is listed the requirement of fire alarm system in different bu8lding occupancy Click to expand... There is nothing in NFPA 72 regarding required fire alarm systems in particular occupancies. In NFPA 101 you will have to look under each occupancy to see what the fire alarm requirements are.
LUIS FERNANDEZ said: Where in NFPA 72 or NFPA 101 is listed the requirement of fire alarm system in different bu8lding occupancy Click to expand... There is nothing in NFPA 72 regarding required fire alarm systems in particular occupancies. In NFPA 101 you will have to look under each occupancy to see what the fire alarm requirements are.