flengineer
Member
- Location
- Miami, FL
I have a ductless minisplit that is installed as supplemental A/C in a kitchen with a larger A/C unit. The minisplit needs to shut off with the fire alarm system. I am specifying a fire alarm relay module to provide the control signal, but can I just have a regular contactor do the shut-off or does it need to be an NFPA 72-approved device (if that exists)? Due to the unit's size, it has no starter. Would it be better to provide a shunt trip breaker (2P15A) at the panel and have the fire alarm disconnect power at the breaker?
Also, am I correct in assuming the relay module will have a negligible affect on the voltage drop of the fire alarm circuit and on the current draw on the battery?
Also, am I correct in assuming the relay module will have a negligible affect on the voltage drop of the fire alarm circuit and on the current draw on the battery?