I'm going to guess !/2 ton and 2000 CFMibew441dc said:I do not have a copy of NFPA 72 in front of me and I need some help.
Air handlers that push air over __________ tons , or_____________CFM require FA shut down ?
Thanks ,
Ibew441dc
Do I get a prize?:grin:mdshunk said:From the IMC:
606.2.1 Return air systems. 2,000 cfm (0.9 m3/s),
Yes. I'll sing you a little song....chris kennedy said:Do I get a prize?:grin:
Well that should keep me from guessing anymore.:roll:mdshunk said:Yes. I'll sing you a little song....
".... Did you ever know that you're my hero? You are the wind beneath my wings..."
mdshunk said:Yes. I'll sing you a little song....
".... Did you ever know that you're my hero? You are the wind beneath my wings..."
The IMC is opposite the requirements contained in NFPA 90A. NFPA 90A requires supply side smoke detection for HVAC systems over 2000 CFM and return side over 15000 CFM.mdshunk said:From the IMC:
606.2.1 Return air systems. Smoke detectors shall be in -
stalled in return air systems with a design capacity greater
than 2,000 cfm (0.9 m3/s), in the return air duct or plenum
upstream of any filters, exhaust air connections, outdoor air
connections, or decontamination equipment and appliances.
606.4 Controls operation. Upon activation, the smoke detec -
tors shall shut down the air distribution system. Airdistribution
systems that are part of a smoke control system shall switch to
the smoke control mode upon activation of a detector.