Fire alarm SLC question

Status
Not open for further replies.

jre257

New User
Location
Indiana
Occupation
Electronic tech
Hello.I have a question about a fire alarm module made by Notifier FMM That appears to be triggering an alarm all on its own,not being attached to the water flow.The resistor is in place,then after about 10 minutes an alarm is triggered.I suspect interference on the SLC line to it.Anyone experience this before.


Thank you
 
I would be more apt to suspect the module. the SLC loop can not create an alarm on its own
Agreed. The SLC loop is like the internet TCP/IP protocol, it can only transport signals, not originate them. Your module has an issue. Replace with same, and if you still have the problem, it may lie with the panel program.
 