I am installing a fire alarm system and have finished running the wire and devicing. I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.
I am installing a fire alarm system and have finished running the wire and devicing. I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.
You could be reading the end-of-line resistors, or the devices themselves if they're already terminated. Otherwise, you should be reading open.I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.
You could be reading the end-of-line resistors, or the devices themselves if they're already terminated. Otherwise, you should be reading open.
If you have a diode test on your continuity checker it will tell you if you are seeing semiconductor devices hooked to the line.I have no shorts to ground, but i read resistance between the conductors.
Ah, now I see. He's measuring end-to-end loop resistance, not conductor-to-conductor. So, he should be measuring wire DC resistance and nothing else. I'd also check each wire to ground.Larry he said 'supply and return' that strongly suggests a class A loop, no EOLs.
I am installing a fire alarm system and have finished running the wire and devicing. I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.