Fire Alarm Testing for shorts and open circuits

Status
Not open for further replies.

bs1224

New member
I am installing a fire alarm system and have finished running the wire and devicing. I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.
 

iwire

Moderator
Staff member
Location
Massachusetts
I am installing a fire alarm system and have finished running the wire and devicing. I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.

Take a look at the panels manual, they usually tell you the maximum loop resistance.
 

nhfire77

Senior Member
Location
NH
I am installing a fire alarm system and have finished running the wire and devicing. I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.

I agree with Iwire read the manual.

What is the reading exactly? Are we talking Mohm?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.
You could be reading the end-of-line resistors, or the devices themselves if they're already terminated. Otherwise, you should be reading open.
 

G._S._Ohm

Senior Member
Location
DC area
I have no shorts to ground, but i read resistance between the conductors.
If you have a diode test on your continuity checker it will tell you if you are seeing semiconductor devices hooked to the line.
The thing with semiconductors is that the resistance they show depends on how much current or voltage your tester puts out. And it is a current-dependent resistance, like incandescent bulbs
and unlike resistors or insulation resistance or conductor resistance.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Larry he said 'supply and return' that strongly suggests a class A loop, no EOLs.
Ah, now I see. He's measuring end-to-end loop resistance, not conductor-to-conductor. So, he should be measuring wire DC resistance and nothing else. I'd also check each wire to ground.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I am installing a fire alarm system and have finished running the wire and devicing. I am wondering what i should be reading for when i test between both the supply and return. I have no shorts to ground, but i read resistance between the conductors.

You will naturally have some resistance from one end of the wire to the other! The typical limit is 100 ohms, divided by the number of conductors. Class B, with two wires would be 50 out and 50 back. Class A is 25 out, 25 back, 25 out, 25 back.

If you have to megger the conductors, don't do this with the devices in place! You'll almost certainly fry any conventional smoke detectors or addressable devices of any kind. Conventional heats and pulls might be OK.
 