C cppoly Senior Member Location New York Sep 7, 2017 #1 Is there a requirement anywhere for fire alarm speaker/strobe circuits have two circuits per floor?
gadfly56 Senior Member Location New Jersey Occupation Professional Engineer, Fire & Life Safety Sep 7, 2017 #2 cppoly said: Is there a requirement anywhere for fire alarm speaker/strobe circuits have two circuits per floor? Click to expand... No, but if you have separate fire areas on the floor you may be required to set each one up as a zone. See 23.8.6.3 et seq in the 2013 edition of NFPA 72.