yorkie

Member
i have a simplex tech that wants me to re pull a 2 cond non shielded in place of the 2 cond shielded i allready have pulled 19 flrs up & dn loop he says he needs a non shielded . i have a shielded pulled if he does not connect the shield or drain wire what does it matter the cable is just for audio on a new simplex mapp net system larry
 
Re: fire alarm

I have made that work in the past. have to cut and tape over all of the sheild splices in every box, as if there is no shield, and make sure that the shield does not accidently ground anywhere.

some of the newer systems are not even using twisted pair for notification.
 
Re: fire alarm

If its audio i would think grounding a shield would be better.What is the impedance of his equipment ? if high that might be the problem
 
Re: fire alarm

Is this a young simplex tech? They tend to hire young guys at slave wages, train them (barely) and then unleash them on unsuspecting clients.
Shielded cable is far superior to non-shielded...just ground the shield at one point only.
Shielded cable is used to minimize RF in speaker cables when there is close proximity to such a source (FM transmitter, etc).
If you can't work with this guy, I suggest you contact the manager at your Simplex field office and see if he has an 'old' tech who can help set things straight.
Trouble is, the 'old' techs are working for Siemens or Notifier or someone who appreciates their abilities and pays them accordingly.
 
Re: fire alarm

Originally posted by thinfool:
Shielded cable is far superior to non-shielded...just ground the shield at one point only.
Shielded cable is used to minimize RF in speaker cables when there is close proximity to such a source (FM transmitter, etc).
Most newer systems are calling out un-shielded cable for the notification circuit (speaker/strob/relay modules). In fact some dont even call for twisted pair, THHN is being used.

I asked my fire alarm goo roo, so i have no code reference, but he said that a sheilded cable with shieleds cut at both ends should act as an unsheilded cable with no adverse effects, but that he would have to look it up to see if this were infact a code violation.
 
Re: fire alarm

What do the job specs. say to pull? That's what I would pull,unless a green sheet is signed for a change order.
 
Re: fire alarm

Originally posted by benaround:
What do the job specs. say to pull? That's what I would pull,unless a green sheet is signed for a change order.
In my opinion this is the best answer given so far.

What where you instructed to pull?

The last Simplex system I did specified unshielded for the speakers and shielded for the strobes. Seemed backward to me but what matters is doing what you are hired to do. :)

If you are going to install fire alarm systems you must check the manufactures cable / condutor requirements first or you may be working for free. :(
 
Re: fire alarm

Originally posted by iwire:
The last Simplex system I did specified unshielded for the speakers and shielded for the strobes. Seemed backward to me but what matters is doing what you are hired to do. :)
I need to correct myself. I talked to my workers. we used shielded for the speakers, and THHN for the strobes, and unsheilded for the pull stations.
 
Re: fire alarm

JB That was on one particular Simplex system.

As far as I know another model Simplex may use fishing line and kite string.

Each FA job I am involved in we get the specific conductor info from the manufacturer before we go to far.

There are just to many types to guess what they want twisted, not twisted, shielded, not shielded, metal raceway or low energy cable. :eek:

That System I described specified using the following cables in metal raceway.

Detectors - Twisted Shielded.

Strobes - Twisted Shielded

Speakers - Twisted
 
Re: fire alarm

iwire, I was correcting myself not you. :)
I agree, with you regarding each job having its own specs making bidding and working them a bit confusing...
 
Re: fire alarm

Originally posted by jbwhite:
iwire, I was correcting myself not you. :)
I did not take it like you where correcting me, I just did not want you to change what you do based on my past experience with Simplex.
:)
 
Re: fire alarm

We use a lot of Simplex 4010 panels, and we are always required to pull twisted shielded cable for all pull stations, smokes, heats & iams. etc.

The horn circuits are 14-2 non shileded or else #14 thhn if in conduit.

Bob
 
Re: fire alarm

Originally posted by iwire:
As far as I know another model Simplex may use fishing line and kite string.
Shame on you Bob. If you read your specs carefully, you would see they call for wet kite string.
 