Fire Alarm

Status
Not open for further replies.

eager2learn

Senior Member
Location
Mennifee,Ca
I would just like to know where in the code book can I find the distance a smoke detector has to be away from duct work as far as A.C. vents and or return air vents etc.
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Without a copy of the NFPA 72, I would venture that this is the document you are seeking.
 

eager2learn

Senior Member
Location
Mennifee,Ca
fire alarm

fire alarm

i checked 760 in the code and couldn;t find it anywhere so i'm assuming that it is in the nfpa 72 - i have also heard that it is supposed to be 3' seperation i just wanted to see it for my self
 

russ

Senior Member
Location
Burbank IL
I thought that this information is in the directions of most smoke detectors.
As mentioned earlier, smoke and carbon monoxide info is usually in the building code.
 

DUCKMAN

Member
ron said:
NFPA 72 used to require 3', but not anymore

That depends on the application.

In a residence, 2007 NFPA 72 11.8.3.5(6) prohibits mounting a smoke alarm or smoke detector within 36 inches of a heat register.


2007 NFPA 72 5.7.1.7 states that detectors be placed "to prevent nusiance alarms" , this does not give a specifoc distance, but allows you to use your good judgement.
 

celtic

Senior Member
Location
NJ
I'd say the NEC article would be 110.3(b) ~ basically...what the manuafc.s instructions say. I would imagine it(the instructions) would coincide with NFPA 72 and all other applicable codes.
 
NFPA 72 A.5.4.7.1 "Detectors should not be located in a direct airflow or closer than 3' from an air supply diffuser or return air opening"

Keep in mind this is from the Annex, which is NFPA 72's version of "Fine Print Notes". It's not a rule, but a recommended practice.
 