517.34 Equipment System Connection to Alternate Power Source.
The equipment system shall be installed and connected to the alternate power source such that the equipment described in 517.34(A) is automatically restored to operation at appropriate time-lag intervals following the energizing of the emergency system. Its arrangement shall also provide for the subsequent connection of equipment described in 517.34(B). [NFPA 99, 3.4.2.2.3(b)]
Exception: For essential electrical systems under 150 kVA, deletion of the time-lag intervals feature for delayed automatic connection to the equipment system shall be permitted.
(A) Equipment for Delayed Automatic Connection. The following equipment shall be arranged for delayed automatic connection to the alternate power source.
~~~~~~
(4) Smoke control and stair pressurization systems, or both.
(5) Kitchen hood supply or exhaust systems, or both, if required to operate during a fire in or under the hood.
~~~~~~
(B) Equipment for Delayed Automatic or Manual Connection. The following equipment shall be arranged for either delayed automatic or manual connection to the alternate power source:
(1) Heating equipment to provide heating for operating, delivery, labor, recovery, intensive care, coronary care, nurseries, infection/isolation rooms, emergency treatment spaces, and general patient rooms and pressure maintenance (jockey or make-up) pump(s) for water-based fire protection systems.
Exception: Heating of general patient rooms and infection/isolation rooms during disruption of the normal source shall not be required under any of the following conditions:
(a) The outside design temperature is higher than -6.7?C (20?F).
(b) The outside design temperature is lower than -6.7?C (20?F), and where a selected room(s) is provided for the needs of all confined patients, only such room(s) need be heated.
(c) The facility is served by a dual source of normal power.
~~~~~~~~~~