There is regulation that states a fire detection alarm panel must be upgraded to class A from Class B if major renovation work is being done. Note that Class A is 4 wire (loop architecture with each set of wires in a separate conduit for survivability during an inadvertant cut of fire cable) and Class B is 2 wire (star architecture).
This includes cable, conduit and panel.
I wonder if it is required to upgrade to Class A from Class B if all that is being done is changing pipes and adding heads to the fire suppresssion system. This is major work to the fire suppression system, but not the fire detection system.
It is possible that some additional wiring will be required (for the fire detection alarm panel) for some zone changes.
This includes cable, conduit and panel.
I wonder if it is required to upgrade to Class A from Class B if all that is being done is changing pipes and adding heads to the fire suppresssion system. This is major work to the fire suppression system, but not the fire detection system.
It is possible that some additional wiring will be required (for the fire detection alarm panel) for some zone changes.