I am currently working in a medical facility. Does anyone know what the code is for fire proofing back boxes IN walls with pads? Electrical code? Building code? Fire safety? Thanks in advance
I am currently working in a medical facility. Does anyone know what the code is for fire proofing back boxes IN walls with pads? Electrical code? Building code? Fire safety? Thanks in advance
I am currently working in a medical facility. Does anyone know what the code is for fire proofing back boxes IN walls with pads? Electrical code? Building code? Fire safety? Thanks in advance
Metallic Outlet Boxes (QCIT) for use infire-resistant rated assembliesAll UL Listed single- and double-gang metallic outlet and switchboxes with metallic or nonmetallic cover plates may be installedin bearing and non-bearing wood stud and steel stud wallswith fire rating not exceeding 2 hours. These metallic boxesare not required to be marked specifically as suitable for use infire-resistant rated assemblies.Metallic boxes located on opposite sides of walls or partitionsare intended to be separated by a minimum horizontal distanceof 24 in. This minimum separation distance between boxes maybe reduced when Wall Opening Protective Materials (QCSN)(commonly known as putty pads) are installed according to therequirements of their Classification.Putty pads other than those installed on the outer surfaces of ametallic box prior to installation of the wall are also available.UL Classified putty pads, also known in industry as box inserts,are for installation on the inside back surface of the box. Thereare also putty pads, known in industry as gaskets, available forapplication under the wiring device cover plate.