I have the following situation.
A client contacts me because they have a fire pump (125hp) connected to their 240V system and the pump is designed to operate at 208V. During the test, the control system triggers a high voltage alarm.
Based on my research in the NEC and NFPA, I have two options.
Please, I await your opinions. Thank you very much
A client contacts me because they have a fire pump (125hp) connected to their 240V system and the pump is designed to operate at 208V. During the test, the control system triggers a high voltage alarm.
Based on my research in the NEC and NFPA, I have two options.
- Install a step-down transformer (240 delta to 208Y) 150KVA. (The issue with this approach is that the transformer, according to NEC, must be protected on the primary side. Since it feeds the fire pump, it should be sized at least 6x FLA, requiring an OCPD of at least 2000A and finding space to place it (there is not much space in the electrical room).
- Replace the pump. (more expensive)
Please, I await your opinions. Thank you very much