Art. 695.6 - Power Wiring
Could anyone help me confirm if Art. 695.6 requirements for power wiring (specifically 695.6(A)(2)d where routed inside the building) apply for BOTH a primary feeder from a utility source and an "Optional" standby generator source? The 2hr. fire rating would be rather easy for the utility source, but difficult for the standby generator feeder. I see an exception to (A)(2)d where the supply conductors for the utility originate within the electrical / pump room, however this is obviously not the case for the standby generator.
From what I can tell....the "optional" source would still be required to meet the same requirements as the utility source.
Thanks in advance,
Could anyone help me confirm if Art. 695.6 requirements for power wiring (specifically 695.6(A)(2)d where routed inside the building) apply for BOTH a primary feeder from a utility source and an "Optional" standby generator source? The 2hr. fire rating would be rather easy for the utility source, but difficult for the standby generator feeder. I see an exception to (A)(2)d where the supply conductors for the utility originate within the electrical / pump room, however this is obviously not the case for the standby generator.
From what I can tell....the "optional" source would still be required to meet the same requirements as the utility source.