Fire Pump Accessory Equipment

Status
Not open for further replies.

wyboy

Senior Member
NEC 295.6 (B)(1) allows conductors supplying fire pumps to supply ?associated fire pump accessory equipment.? If the fire pump is located in a vault designated for the fire pump, can a circuit for the light and service receptacle be tapped off conductors supplying the fire pump in the vault if all other requirements for taps are met. Another words, is a light and receptacle in the fire pump vault considered associated fire pump accessory equipment?
 
2008 NEC, section 695.(B) Fire pump supply conductors on the load sie of the fi..... (sentence #2 states "They shall supply only loads that are directly associated with the fire pump system........
 