Hello. This falls under 2011 NEC. We have a fire pump where the controller is fed directly from a utility meter/main. The inspector is telling us that we need to use an Instantaneous Trip CB (ITCB) in this application in order to comply with both 695.4(2)(a) AND table 430.52. I do not see any way to use an ITCB in this case as it's not listed in combination with the downstream fire pump controller. What I can't figure out and I'm hoping someone else can, is how to show that the 250% of FLA for an inverse time CB doesn't apply in the case of a fire pump, where the CB is sized based on locked rotor. Nothing that I can find in either section mentions an exception for the other. I see his point, he sees the 800% for an ITCB and the 250% for an inverse time CB and says, "well you can only meet the locked rotor requirement of 695.4 AND the FLA requirement of 430.52 with an ITCB. I do know that ITCB's have been rejected from previous code cycles and are now being included under a very limited exception for FP's under 2014. Any help here? Thanks.