Attached sketch shows utility Poco service conductors Srvc B tapped off of line side emergency compartment of main service switchboard ahead of six main service disconnect
The Srvc B conductors feed fire pump service rated controller but in trough connect to service conductor Srv C in trough. The Srv C service conductors feed the jockey pump service rated.
There are no backup generator and there is no overcurrent protection line side of jockey oump controller sefvice rated.
Questions:
1. Does NEC 2017 section 695.4(B)(2)(a)(1) says to size overcurrent protection based off of LRC of jockey pump and fire pump. However there is no overcurrent protection provided and they are all in fire pump controller and jockey pump controller. Would 695.4(B)(2)(a)(1) apply inside of the controllers? If yes then how can one check OCPD inside controllers?
2. Jockey pump circuit would it require outside OCPD since the rules of NEC 2017 section 430 apply or if the controller has OCPD this would be acceptable?
I had similar versions of this post earlier but this post is regarding OCPD of jockey pump controller so it is different then previous post
which involve grouping of disconnects and more than six disconnects (not this post)
The Srvc B conductors feed fire pump service rated controller but in trough connect to service conductor Srv C in trough. The Srv C service conductors feed the jockey pump service rated.
There are no backup generator and there is no overcurrent protection line side of jockey oump controller sefvice rated.
Questions:
1. Does NEC 2017 section 695.4(B)(2)(a)(1) says to size overcurrent protection based off of LRC of jockey pump and fire pump. However there is no overcurrent protection provided and they are all in fire pump controller and jockey pump controller. Would 695.4(B)(2)(a)(1) apply inside of the controllers? If yes then how can one check OCPD inside controllers?
2. Jockey pump circuit would it require outside OCPD since the rules of NEC 2017 section 430 apply or if the controller has OCPD this would be acceptable?
I had similar versions of this post earlier but this post is regarding OCPD of jockey pump controller so it is different then previous post
which involve grouping of disconnects and more than six disconnects (not this post)