I have a Water treatment building that contains a fire pump that will be serving two big box retail stores (the fire pump will supply fire water to both buildings). The owner would like to have a single emergency feeder feed the water treatment building from one of the big box retail stores. Would a single feeder meet the requirements of 695? Specifically the requirements listed below?
1) The requirement for Two sources of power.
2). The requirement that no other loads, other than the fire pump, be off of the fire pump feeder (the water treatment building will also have lights, receptacles, water booster pumps, etc).
3). The requirement that no Overcurrent Protective Device be installed on the fire pump feeder (the feed will come from an emergency distribution panel feeder breaker).
4.) The requirement that no ground fault protective device be installed in the fire pump feed (the normal utility panel for the big box retail store has a GFP in it)
The only way I can think to meet 695 would be to bring two feeds from the bix box retail building, one from the emergency distribution panel and one from a tap on the secondary of the big box retail building's utility transformer. At the water treatment building, the normal feed would then be brought to a wireway outside the building with two taps going into the building, one for the fire pump, and the other to the buildings main panel which would feed the rest of the building's loads. Would this meet 695?
1) The requirement for Two sources of power.
2). The requirement that no other loads, other than the fire pump, be off of the fire pump feeder (the water treatment building will also have lights, receptacles, water booster pumps, etc).
3). The requirement that no Overcurrent Protective Device be installed on the fire pump feeder (the feed will come from an emergency distribution panel feeder breaker).
4.) The requirement that no ground fault protective device be installed in the fire pump feed (the normal utility panel for the big box retail store has a GFP in it)
The only way I can think to meet 695 would be to bring two feeds from the bix box retail building, one from the emergency distribution panel and one from a tap on the secondary of the big box retail building's utility transformer. At the water treatment building, the normal feed would then be brought to a wireway outside the building with two taps going into the building, one for the fire pump, and the other to the buildings main panel which would feed the rest of the building's loads. Would this meet 695?