dvcraven0522!
Member
- Location
- St. Louis
- Occupation
- Electrical Design
I have attached a a one line sketch showing utility xfrm. feeding a MDP with full generator back up.
It is my understanding I am allowed to feed a fire pump circuit as shown on the CB #1 from the MDP as shown. The only requirement is that this circuit breaker shall carry the the locked-rotor current of the FP motor. But the conductors to this FP are only require to be sized for 125% of the FP motor FLA. Is that correct?
Thanks
Dan Craven
It is my understanding I am allowed to feed a fire pump circuit as shown on the CB #1 from the MDP as shown. The only requirement is that this circuit breaker shall carry the the locked-rotor current of the FP motor. But the conductors to this FP are only require to be sized for 125% of the FP motor FLA. Is that correct?
Thanks
Dan Craven