Fire pump Code letter
binwork91
new york
electrical engineer
When sizing the fire pump OCPD, we use Table 430.7(B). My problem is that I cannot find the code letter in the submittal.
Can anyone provide a screenshot from any fire pump submittal that shows the code letter?
I know nameplate of fire pump must have this information, but it is not installed yet.
Look at this thread for an example
I recently looked for code letters for 25 HP 3-phase motors and found most of the standard motors had a code letter of "G", but most of the listed fire pump motors of the same size had a code letter of "F". However in both cases there were variations with one of the standard motors having a code letter of "M" and one of the fire pump motors having a code letter of "G".
You are going to need the data from the motor manufacturer or a picture of the nameplate to be sure.
Thank you. However, this one shows the nameplate. I only have the submittal, and the fire pump is not on site yet.
Is there any way to determine the code letter from the submittal, or does the submittal not provide the code letter?