Re: Fire Pump Conductor Size
The quick answer is no. The conductors will not have enough time to get hot enough to be damaged; they will be protected by the fire pump controller. However, the controller must have the ability to allow the fire pump to run to failure. In other words, the winding of the motor will burn up before the conductors are damaged.
The OCPD (if provided) must carry LR indefinitely. The service disconnect (if provided) must carry 115% of the running amperes of the largest motor plus 100% of the rest of the load. The motor circuit conductors must carry 125% of the running amperes of the largest motor plus 100% of the rest of the load. The overloads are in the fire pump controller and will allow the motor to run to failure before opening up to protect the motor circuit conductors and other upstream equipment. Under LR conditions, the controller OL's will open after about 20 seconds.
Sorry, I didn't expect to get that long winded.