Al Pike
Member
- Location
- Honesdale, Pa
I have a 150 HP Fire Pump that's 70 ft from a 3000A service. The Engineer has me installing (4)sets of (3)500mcm and a 3/0gnd in 4in RGS from the FPCP ATS to the service and (1) set of 3-600mcm and a 1/0gnd to the Generator ATS's splice for the Fire Pump feeders. The conductors to the service will be tap'd off of the bus and the generator is tap'd after the 1200A OCPD in a splice box inside the building onto (2) set's of 600mcm w/1/0 gnd that feeds 2 ATS's. The Jockey Pump will be tap'd the same way.
695.6(B)
150hp (430.250)=180A
180A*1.25= 225A
Other than associated loads calculated in why would I have to run anything bigger than 4/0? VD ok but will have to calculate generator after final location.
When I questioned the math I made it worse and was told that I have to size the wires to the generator to the OCPD of 1200A since the breaker size changed. That means they now want (3) sets of 600mcm to the splice.(I'm not sure the splice meets 700.10(B) either.
This is alot of copper to feed a 225A pump.
Thanks for the help