I'm installing a fire pump 50 hp 208 v, according with the table 430.250 the FLA is 143 amps.
Then 143 amps x 1.25= 178.75 amps, I suppose to use one 3/0 per phase, but the fire pump control had a wye /delta configuration contact relays ( M1, M2 ) that feed the fire pump.
Because of this configuration I know that I have to run two set of cables in one conduit from the fire control panel to the pump but I'm little bit confused if have to use two set of 3/0 or divide the FLA in two and run 2 set of let's say #1 which will give about 200amps.
Please help, will appreciate....thanks.
J Pujols.