I want to confirm my understanding of Art. 695. I'm sizing my POWER SOURCE i.e POCO transformer to hold the locked rotor current of the fire pumps, plus jockey maintenance pump, plus ancillary equipment i the pump house. However the conductors feeding the motors are sized per Art. 430 at no less than 125%. So if there is a locked rotor event the transformer will hold the increased current, but eventually the motor and/or the conductors will melt. Are the secondary conductors from utility transformer sized off of "normal" calculation based Art. 220 & 430 calculated to 208A or sized to hold the 1158A based off of Locked rotor current?
Here is my scenario:
150HP Fire Pump = Locked Rotor Current of 1123A (Art 430 Full load amps= 180A)
1.5HP Jockey Pump = Locked Rotor Current of 10.2A (Art. 430 Full load amps= 3A )
Ancillary Loads = 25 Amps
Total Lock Rotor + Ancillary Loads = 1158.2A (961KVA)
Full Load Currents + Ancillary Loads = 208A
Here is my scenario:
150HP Fire Pump = Locked Rotor Current of 1123A (Art 430 Full load amps= 180A)
1.5HP Jockey Pump = Locked Rotor Current of 10.2A (Art. 430 Full load amps= 3A )
Ancillary Loads = 25 Amps
Total Lock Rotor + Ancillary Loads = 1158.2A (961KVA)
Full Load Currents + Ancillary Loads = 208A