Perhaps this will help. A fire pump service is just that, a service, albeit a special one. Since you are connecting in front of the normal service disconnecting means, you are installing service entrance conductors and not a feeder to the fire pump. In general, all of the conductors and switches are sized no differently than for any other motor until you get to the overcurrent protection. You may install short circuit and ground fault protection but not overload protection. The fire pump controller provides a modicum of overload protection. If the fire pump controller is SUSE (suitable for use as service equipment) rated, you don't need to provide short circuit and ground fault protection. However, since this is service equipment, you are require to provide a main bonding jumper. You can spend all day looking up code references but you already know the answers if you look at the big picture. :smile: