Ithinkimstillhere
Member
- Location
- saint louis
I have a new service entrance rated switchboard in the basement of a historical structure. The basement is completely exposed. The service meter is internal to the board and a fire pump is connected ahead of the main breaker. In my documents I indicated that the conduit needs to be concrete encased from the termination at the switchboard, all the way to the fire pump (unless its ran outside-which is impossible).
Contractor is stating that it's impossible for them to concrete encased conduit in the ceiling space of the basement and asking if they can just run RMC. As I understand it, given we can't physically run these conduits outside, they have to be concrete encased, unless I'm missing something here.
Contractor is stating that it's impossible for them to concrete encased conduit in the ceiling space of the basement and asking if they can just run RMC. As I understand it, given we can't physically run these conduits outside, they have to be concrete encased, unless I'm missing something here.