I have a question we have three 500 kw generators 480 volts 3 ph each generator is connected in a paralleled system these feed a switchboard which has 6 sections a 400 amp 600amp 800amp 1200amp 800amp emergency power . The 6th section is the main buss section fed from all generators which has no main breaker .
We have one fire pump ATS which the emergency feed is tied directly to section 6 buss ahead of all breaker sections then it goes to the FP ATS . Each genset has a 800amp breaker the inspector has ask me to have a fire alarm monitor the position of each genset main 800amp which are internal to the generator factory install .
What code rule or section covers this requirement I cant find it and he didn't give that to me yet said he had to look into it but id like to find it before hand .
We have one fire pump ATS which the emergency feed is tied directly to section 6 buss ahead of all breaker sections then it goes to the FP ATS . Each genset has a 800amp breaker the inspector has ask me to have a fire alarm monitor the position of each genset main 800amp which are internal to the generator factory install .