I have three generators with paralleling gear that feed an emergency switchboard. I need to feed a fire pump, life safety loads, standby loads and optional loads from the generator. Under 2008 NEC, I believe I need to provide the breakers for the LS, SB and OP loads each in a separate section of the switchboard to comply with 700.9(B)(5).
However, how can I feed the fire pump and comply with 695.4(A)?
695.4(A): The supply conductors shall directly connect the power source to either a listed fire pump controller or listed combination fire pump controller and power switch. Where the power source is supplied by on-site generator(s), the supply conductors shall connect to a generator disconnecting means dedicated for the purposes of serving the fire pump. The disconnecting means shall be located in a separate enclosure from the other generator disconnecting means.
I can't tap into the feeder before the switchboard since there are three different generators. Does this not apply if there is a direct connection from a utility and the generator is the secondary source?
However, how can I feed the fire pump and comply with 695.4(A)?
695.4(A): The supply conductors shall directly connect the power source to either a listed fire pump controller or listed combination fire pump controller and power switch. Where the power source is supplied by on-site generator(s), the supply conductors shall connect to a generator disconnecting means dedicated for the purposes of serving the fire pump. The disconnecting means shall be located in a separate enclosure from the other generator disconnecting means.
I can't tap into the feeder before the switchboard since there are three different generators. Does this not apply if there is a direct connection from a utility and the generator is the secondary source?