lkdiaZ
Member
- Location
- Virgin Islands
- Occupation
- Electrical Contractor
Application: Facility is adding a fire pump in basement of 3 story building. Generator building is several hundred feet away in a separate structure. The generator is existing and there's an existing ATS that is getting replaced by 4 ATS'. There's control wire from the existing ATS to the generator for auto start/stop.
Question 1. Does the control wire from the fire pump have to be 2 hour rated? I think yes but looking for feedback. I'm not seeing where it excludes the rating while in the pump room or while in the electrical room so I'm assuming it has to be 2 hr rated until it leaves the building.
Question 2. Do we have to run control wire from fire pump controller to the generator directly or can we wire in series with the other ATS' that will be installed and make use of the existing control wiring between the 2 structures. ATS' will be wired so that contact opening starts generator.
Thanks for any feedback.
Question 1. Does the control wire from the fire pump have to be 2 hour rated? I think yes but looking for feedback. I'm not seeing where it excludes the rating while in the pump room or while in the electrical room so I'm assuming it has to be 2 hr rated until it leaves the building.
Question 2. Do we have to run control wire from fire pump controller to the generator directly or can we wire in series with the other ATS' that will be installed and make use of the existing control wiring between the 2 structures. ATS' will be wired so that contact opening starts generator.
Thanks for any feedback.