Feeders from the service switchgear to the fire pump controller is tapped ahead of the main in a separate vertical switchgear enclosure. Fire pump is 480 volts.
I am told that we need to run a neutral, along with the 3 phases from the switchgear to the fire pump controller, even though the neutral is not being used. The bonding is done in the service switchgear. Therefore I argue that the service point is in the switchgear, and the neutral is not required at the fire pump.
Where in the NEC does that states this requirement of running the neutral required at the fire pump?
I am told that we need to run a neutral, along with the 3 phases from the switchgear to the fire pump controller, even though the neutral is not being used. The bonding is done in the service switchgear. Therefore I argue that the service point is in the switchgear, and the neutral is not required at the fire pump.
Where in the NEC does that states this requirement of running the neutral required at the fire pump?