hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have one utility service going to main service switchboard. The main service switchboard has a tap ahead of main service breaker in one of the compartment which has service conductors going straight to Fire pump controller service rated which then feeds fire pump. See attached riser
The fire pump service rated is in basement opposite corner from main service switchboard 1st floor. See attached floor plan.
See attached below grounding details. The conductor labeled FP GEC bubble in attachment should it go to ground rods as shown or should it go to external ground bus bar GBB? It is not clear what NEC 2017 says. Designer says by placing FP GEC at external GBB creates ground fault current path but i dont see how this is possible. I think their is ground fault current path from the current configuration from switchboard to GBB to steel to rods to FP comtroller. What are your thoughts? Where should FP GEC be?
The fire pump service rated is in basement opposite corner from main service switchboard 1st floor. See attached floor plan.
See attached below grounding details. The conductor labeled FP GEC bubble in attachment should it go to ground rods as shown or should it go to external ground bus bar GBB? It is not clear what NEC 2017 says. Designer says by placing FP GEC at external GBB creates ground fault current path but i dont see how this is possible. I think their is ground fault current path from the current configuration from switchboard to GBB to steel to rods to FP comtroller. What are your thoughts? Where should FP GEC be?