ronball

Senior Member
Location
Champaign Il.
Occupation
Electric Contractor
Is their any special wire to be used from controller to fire pump. Will only be going about 6 ' from controller to pump.

Can Greenfield conduit be used for this , if only 6' or less? Running 4/0 copper / for 75 hp 3 phase 208 pump.

Thx
Ron
 
Something off here. 75 HP @208 across the line starting needs conductor ampacity of 264 amps.
Yup that's what I was thinking, from T430.250 the FLC is 211*125%=264. If the terminals are only rated for 250 kcmil they're too small because the minimum conductor size is 300 kcmil unless it's a Wye start/Delta run controller then:

FLA*58%*125%=211*.58*1.25=153 amps with (6)-#2/0 conductors to the motor.
 
Yup that's what I was thinking, from T430.250 the FLC is 211*125%=264. If the terminals are only rated for 250 kcmil they're too small because the minimum conductor size is 300 kcmil unless it's a Wye start/Delta run controller then:

FLA*58%*125%=211*.58*1.25=153 amps with (6)-#2/0 conductors to the motor.
I agree. And the math works for all 6 to be in one LT flex to the motor.
 